A simplified description of commonly used Earthing systems in the United Kingdom,
along with a basic diagram of the most common,
** note, :- extending the PME system outside the equipotential zone has been OMITTED from the diagrams as it is considered IMHO to be outside the remit of a simplified description of earthing systems and is dependant on a number of varying factors that could only be established via a site visit and survey, and would also be dependant on the electrician concerned being wholly conversant with the inherent risks etc thereof and understanding the principles of earthing systems and how they work and intermix with each other.
TNC-S and PME
The subtle differences.
TN earthing systems in the UK are always earthed at the supply transformer, a TN-S system utilizes a separated PE conductor throughout its length, The TNC-S system utilizes the neutral conductor, PEN , which is earthed at the supply transformer, and then separated at the consumers point of supply.
A PME system, utilizes the neutral just as the TNC-S does, but is earthed at intervals throughout its length, and more importantly, to be fully PME, should be earthed at point of, or just before the consumers point of supply.
PME earthing is still an ongoing upgrade to the older TNC-S earthing system, the supply companies still have some time to bring all TNC-S systems in line (2012).
The debate would be, if no earth electrode is supplied at the end of the distributors cable, does it still comply with PME? To understand this we would have to know why this last earth electrode is important to the integrity of the true PME.
Broken neutral on TNC-S systems.
The fact is, whilst possible, this is still a rare occurrence, however it should not be excluded, indeed the supply companies take the possibility very seriously, otherwise why would they be converting to PME.
In the event of a broken neutral the fault paths will have no defined route, and will migrate to and from all users on the same system, this can give rise to dangerous voltages on the neutral conductor.
One of the main protective conditions of this type of fault is the correct bonding within the installation, however this is becoming near on impossible due to the utility companies now supplying their services with plastic pipes. There will always be a leakage to earth, to some extent, but not enough to clear most dramatic faults of this nature.
PME systems are designed to lower this possible fault, and to provide at least a connection with earth, at one, or multiple points. For this reason it is important to have an earth electrode close to, and not shared with another installation, if designed this way, any neutral faults will always have a path to earth, and whilst the fault can still be shared, the voltages on the neutral will not be allowed to rise as high ,with multiple earth electrodes at each installation point.
Using PME to extend the equipotential zone.
It is possible to extend the equipotential zone of a true PME system, with correct design, and can sometimes be confused for a TT system. Remember PME stands for Protective Multiple Earthing.
The neutral conductor is still connected throughout the system, however earth electrodes could be introduced a various points within the installation, and connected to the main earthing terminal at origin, or separated to provide protection in those circuits, providing multiple points of reference to earth. This type of arrangement must be fully compliant with all regulations, and the earthing within the installation should be verified to ensure continuity throughout.
along with a basic diagram of the most common,
** note, :- extending the PME system outside the equipotential zone has been OMITTED from the diagrams as it is considered IMHO to be outside the remit of a simplified description of earthing systems and is dependant on a number of varying factors that could only be established via a site visit and survey, and would also be dependant on the electrician concerned being wholly conversant with the inherent risks etc thereof and understanding the principles of earthing systems and how they work and intermix with each other.
TNC-S and PME
The subtle differences.
TN earthing systems in the UK are always earthed at the supply transformer, a TN-S system utilizes a separated PE conductor throughout its length, The TNC-S system utilizes the neutral conductor, PEN , which is earthed at the supply transformer, and then separated at the consumers point of supply.
A PME system, utilizes the neutral just as the TNC-S does, but is earthed at intervals throughout its length, and more importantly, to be fully PME, should be earthed at point of, or just before the consumers point of supply.
PME earthing is still an ongoing upgrade to the older TNC-S earthing system, the supply companies still have some time to bring all TNC-S systems in line (2012).
The debate would be, if no earth electrode is supplied at the end of the distributors cable, does it still comply with PME? To understand this we would have to know why this last earth electrode is important to the integrity of the true PME.
Broken neutral on TNC-S systems.
The fact is, whilst possible, this is still a rare occurrence, however it should not be excluded, indeed the supply companies take the possibility very seriously, otherwise why would they be converting to PME.
In the event of a broken neutral the fault paths will have no defined route, and will migrate to and from all users on the same system, this can give rise to dangerous voltages on the neutral conductor.
One of the main protective conditions of this type of fault is the correct bonding within the installation, however this is becoming near on impossible due to the utility companies now supplying their services with plastic pipes. There will always be a leakage to earth, to some extent, but not enough to clear most dramatic faults of this nature.
PME systems are designed to lower this possible fault, and to provide at least a connection with earth, at one, or multiple points. For this reason it is important to have an earth electrode close to, and not shared with another installation, if designed this way, any neutral faults will always have a path to earth, and whilst the fault can still be shared, the voltages on the neutral will not be allowed to rise as high ,with multiple earth electrodes at each installation point.
Using PME to extend the equipotential zone.
It is possible to extend the equipotential zone of a true PME system, with correct design, and can sometimes be confused for a TT system. Remember PME stands for Protective Multiple Earthing.
The neutral conductor is still connected throughout the system, however earth electrodes could be introduced a various points within the installation, and connected to the main earthing terminal at origin, or separated to provide protection in those circuits, providing multiple points of reference to earth. This type of arrangement must be fully compliant with all regulations, and the earthing within the installation should be verified to ensure continuity throughout.