My living room sockets which are on a ring main circuit (all sockets run off a single 32amp breaker) are all connected using old imperial cable (2.5mm is the equivalent).

I want to move a socket higher (not spur) so I plan on removing the socket and using Wago inline connectors to extend new cable so it runs up the wall to a new socket.

Question is given the earth (CPC) cable is now 1.5mm and I'm told the old imperial earth cable is 1.0mm, can these earth differing sizes be used on the same circuit? I've did a new socket as a spur about 8 years ago and have never had any issues?
 
Hi Tom, thank you for your response.

So given it's a ring circuit the previous socket in the chain is providing load to the socket I want to move (sorry not trying to teach you how to suck eggs it's more to explain myself!)

So I'm going to use Wago inline connectors as per diagram.
 

Attachments

  • Untitled presentation (3).jpg
    Untitled presentation (3).jpg
    29.8 KB
  • Screenshot 2024-10-28 at 17.33.43.png
    Screenshot 2024-10-28 at 17.33.43.png
    39.9 KB
@kerching is asking what type of box are you going to house the wago's in and where?

Why not leave the existing socket where it is and run a spur from that to the one higher up?
 
Stored in the inline Wago boxes, secured to the joists.

It was my very first thought to spur off the existing socket but other would it not overload the socket? Certainly would be crowded with 3 sets of each cable in each L, N and E.
 

Attachments

  • Screenshot 2024-10-28 at 17.55.26.png
    Screenshot 2024-10-28 at 17.55.26.png
    73.3 KB
I thought you were planning to move an existing socket up the wall but in much the same place, which would mean jointing 2 cables in the wall. If you are doing more work so you can do the jointing under the floor then it is a lot easier to get what you want, with more chasing and more making good afterwards.
 
At least it's nicer than Harry's and Tom brother...:ROFLMAO:
I never chose that avatar, I was happy with what I had. Some previous mod admin who thought it was amusing changed it when I mentioned southern softies and Essex girls in white shoes dancing around their handbags. The Kleenex bit may be referring to a female TV person who has a crush on me Avatar has been like that for years now and I quite like it
 
My living room sockets which are on a ring main circuit (all sockets run off a single 32amp breaker) are all connected using old imperial cable (2.5mm is the equivalent).

I want to move a socket higher (not spur) so I plan on removing the socket and using Wago inline connectors to extend new cable so it runs up the wall to a new socket.

Question is given the earth (CPC) cable is now 1.5mm and I'm told the old imperial earth cable is 1.0mm, can these earth differing sizes be used on the same circuit? I've did a new socket as a spur about 8 years ago and have never had any issues?

Some common errors with DIY alterations to sockets that I come across all too often are where the persons doing the work assumes;

(a) Sockets must be wired as ring..... they do not!
(b) Sockets must wired with 2.5mm T&E.... they do not!
(c) Sockets must be supplied by a 32A MCB.... they do not!
(d) Because there are two cables connected at a socket or an MCB then it must be a ring.... it may not be!
(e) Because something is working it must be good, safe, and electrically robust enough to be extended.... it may not be!

Whereas reality is more like:-
A 4.0mm 32A radial, or a 2.5mm 20A radial may be a better, more economical and safer solution for many socket circuits.

A broken ring circuit can appear to work but it leaves many potential dangers, and it should never be amended / extended without first confirming the ring integrity and correcting all anomalies found prior to doing any alterations.

For many years now there has been talk of removing ring circuits from the wiring regulations.. There are very much a UK oddity, and there are safer more practical wiring arrangements for sockets that can be used.

Very few people undertaking DIY electrical work have any knowledge of the importance of a circuits "Earth Loop Impedance" and the maximum permissible values to ensure that the circuit protective devices will operate fast enough.

The size of the live conductors and the earth CPC have direct effect upon the Earth Loop Impedance.

So..
{A} If you have proved that the ring is intact and it is within the max Earth Loop Impedance values then mixing the 1.0mm & 1.5mm should not be a problem...

{B} If you circuit is only providing a handful of low power requirement sockets, then you could be better converting it to a 20A radial and save yourself all the faff of extending & testing the ring! (Excluding Kitchens and Utilities, very few rooms in the average domestic house actually need a 32A socket circuit!)

Please also remember Wago's are great.. But they do all have a maximum current rating they are designed to operate with..
NOT all Wago's have the same current rating!

Choose your Wago wisely! :)(y)🍻
 
Stored in the inline Wago boxes, secured to the joists.

It was my very first thought to spur off the existing socket but other would it not overload the socket? Certainly would be crowded with 3 sets of each cable in each L, N and E.

I wouldn't choose one of those Wago Boxes for extending 2.5mm T&E's....
They can sometimes be ok for a few 1.0mm / 1.5mm T&E lighting circuits...

But IMHO its pushing it a bit for a secure 2.5mm joint.
 
I've opted for the plug sockets with the MK sockets with the Wagos. It seemed the safest and easiest install, all be it for the cost!

If you think you will struggle with 3 x 2.5s then get an MK socket with built in Wagos…..they’re expensive BUT will do the job