  1. M

    Eicr Problem

    Yes I do no how dangerous it is the board was isolated at the sub prior to neutrals removed
  2. M

    Eicr Problem

    Sorry switches to DB's closed testing L-N 240volts
  3. M

    Eicr Problem

    All switches are closed and neutral conductor is removed from switch if I measure live of db A to neutral of db a =240 volts if I measur live of db a to neutral bar if db b I get 240volts both fuse boards are in same enclosure
  4. M

    Eicr Problem

    The earthing system is tn-s if the neutral is removed from main switch I get 240volts from live of main switch and neutral bar
  5. M

    Eicr Problem

    DB A and B both isolated by main switch remove neutral from main switches put one probe on incoming live conductor in main switch and other probe on neutral bar of A or B there is then no return path for the neutral as DP main switch is isolate but still getting 240 volts live to neutral
  6. M

    Eicr Problem

    I've been testing a army accommodation block I have 8 x Merlin gerin fuse boards which have two supply's effectively two dis boards in one metal enclosure 16dbs in total they have two main switches double pole supply cable to boards is two core 16 mm swa incomer is 120mm 4core armour no surface...
  7. M

    4mm ring

    The subbys in question would see two 4mm cables on a breaker and straight away would not even consider to test for a ring (they work for a large testing company,the more they test the more they earn )
  8. M

    4mm ring

    The reason I asked is that we are testing a accommodation blocks on an army camp and have 100+ rings to test most are wired 4mm single live and cpc should I keep testing the rings or not. one block the Zs was excessive on all the rings but was protected by a rcbos do I test the ring or not!!
  9. M

    4mm ring

    Hi,I just wonder if how many of you would test a 4mm ring for ring continuity .The reason I ask is that a chap I work with testing has said a lot of sub contractors don't test 4mm ring as it can carry 32amps if the ring was broken.i my self have always tested ring regardless of conductor size...
  10. M

    Harry Patch

    I met Harry patch in the care home he was in, in wells Somerset a few years ago.what a great guy he was
  11. M

    PEFC & PSCC

    +1 Your merger will test phase to phase safely
  12. M

    IP rating

    Yes they are the old lights are explosion fittings but the switches are just standard types thanks anyway
  13. M

    IP rating

    Hi, does anyone know or where I can find what the IP rating of lights and switches should be for a room containing a vented battery system for emergency lighting.the building is for a theatre on a army camp the istallation is 40 years old,cheers .
  14. M

    I found a "made up" PIR today.

    I've had a company test circuits and dis boards that did not exist in a building I've seen it so many times,that's why they charge
  15. M

    PAT company caught out again

    What the pat testing company's have got Is a pattiling gun that fire labels on to appliances at will. I use to work for a company that wanted you to test 250 items a day !!!!
  16. M

    strangeness......

    I was checking smokes for a housing association,knocked on a door in a block of flats.took the tenant ages to answer when he did he said he was in the shower.he was very large and had a towel around him.he said come on in and turned around as he turned the towel did not cover his arse and he had...
  17. M

    Slightly High Zs

    If you have a B32 mcb if Zs has been exceeded greater than 80% value of 1.44ohms you have to do a live neutral loop reading.if this is less than 1.44ohms then it will disconnect in less than 0.4 sec under short circuit conditions
  18. M

    new testing exam

    The reason why it has a low pass rate is its the hardest electrical exam to pass.Ive been testing full time for the last 12 years .Im alway learning and coming across things I've never seen before .It should be made harder not easier by making it multi choice.maybe the C&G are doing it for...
  19. M

    Taking the peas

    It must be a testing company I use to work for one, you be expected to test both property's in 3days while it was occupied Zs reading only and make the rest up!!!!