    RCD earth potential

    Testing Ze does not prove polarity, Ze is the resistance of the incoming earth. Dead testing is not just testing the resistance of the incoming earth. The continuity dead tests prove polarity of the internal circuits  and the polarity live test proves the polarity of the incoming supply. You are...
  2. S

    RCD earth potential

    Some of you seem to want to discuss electrical stuff and offer helpful advise. A question to thoes people, is it just me, or do you think there are some people who come in here just  to troll others?
  3. S

    RCD earth potential

    If you think Ze confirms polarity you need locking up
  4. S

    RCD earth potential

    It was noted the RCD did not trip, there would have been a leakage current from line to earth, if greater than 30mA, the RCD should have tripped. I dont think necessarily the MCB would trip, this would depend upon the resistance between the bridge the nail was making and the value of Zs
  5. S

    RCD earth potential

    Thank you very much for your advice. I have listened to advice related to the actual fault, if you look back when polarity was mentioned, I commented that reversed polarity made allot of sense. Most of the other "advise" has just been insults and telling me how wrong and stupid I am When I go...
  6. S

    RCD earth potential

    Why is this so hard? You are all experienced electricians. We had a potential difference between neutral and earth, the thinking was the nail had cut through the installation of the line and was making a connection between line and earth, making the earth live
  7. S

    RCD earth potential

    After the meter there is an isolation switch, reversed thewre
  8. S

    RCD earth potential

    What question have I not answered? Good
  9. S

    RCD earth potential

    My attitude is a response, I am being attacked, I am responding to vicious, insulting attacks. I am not the one initiating the insults. We were not commissioning the installation we were fault finding.
  10. S

    RCD earth potential

    Is this a legit electricians forum or is a place trolls hang out? your opinion means nothing to me
  11. S

    RCD earth potential

    Please do not comment on this thread, you have not read anything I have written, you are insulting and your comments are not helpful
  12. S

    RCD earth potential

    It was not a nail driven through a cable and we would have found it in 5 minutes if it was. What is your point? Your comment is very insulting and not helpful at all Polarity at the distributor's  isolation switch
  13. S

    RCD earth potential

    Thank you very much for your invaluable advice and passing your experience on to me :)
  14. S

    RCD earth potential

    We did not sign the installation off, we knew the symptoms of the fault on the circuit. The installation is not in commission A full series of tests will be done before the installation is brought into commission. Rome was not built in a day. We had to diagnose the fault before doing a full...
  15. S

    RCD earth potential

    I know you cannot verify polarity by looking at the cable colours, I find your comment very patronising, I have passed the C&G inspection and testing exam, as I have previously stated. The electricians I was working with are very experienced and skilled, I find your comment very insulting...
  16. S

    RCD earth potential

    You are very opinionated, the electricians I worked with are not incompetent.  We didnt do the rewiring, as you rightly pointed out, polarity along with all the other tests should have been carried out before the board was energised, this would lead an intelligent person to assume something...
  17. S

    RCD earth potential

    Well we didnt get there till quite late in the day, we ran out of time, the two electricians started investigating the ring mains 1st, maybe an error on their behalf, they found a fault in the ring mains. It was a case of more than one fault.  I guess from their experience they knew what that...
  18. S

    RCD earth potential

    Line to earth was 0V
  19. S

    RCD earth potential

    Well it was not actually a MET. Main earth came from distributors fuse box to a terminal, from terminal to consumer unit. There was continuity from that terminal to the consumer unit, I will do a Ze test tomorrow to be sure, thank you