  1. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Just like the vast majority of the sellers/manufactures do.
  2. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    I don't think anyone would be jealous of the crap I have to deal with most days.
  3. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Reverse polarity could be one. The lack of overcurrent protection on the N. The N contacts are more like a simple switch, rather than having the same breaking capacity as the L side. As already said, in most scenarios it won't make much difference.
  4. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Double pole disconnects both the live and neutral wires for full isolation. Sp+N Is not considered to be a true double pole device, as it doesn't control two separate circuits simultaneously.
  5. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    That isn't 2 phases, it's two halves of the same 110V single-phase.
  6. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Typically, a 2 phase supply used a Neutral, hence you couldn't achieve complete isolation using 2 poles.
  7. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    @poni said: Double pole is for two phases circuits. A DP MCB can be used on single phase and provide isolation. A DP (Double Pole) MCB on a 2-phase supply would not provide complete isolation. @nicebutdim correctly said that the difference is: SP+N lacks overcurrent protection on the neutral.
  8. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    722.531.3.1 RCDs shall disconnect all live conductors. As @nicebutdim check with the manufacturer as to the requirements.
  9. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Where would the Neutral conductor terminate to give isolation ?
  10. mainline

    Difference between "Single pole with switched neutral" AND "Double Pole" ?

    Dp (sp+n) rcbos are helpful where you have a N+E fault as sp ones won't clear the fault, particularly on TT earthing where an upfront rcd is being used.
  11. mainline

    Would this be a C3 on next EICR

    It's not an improvement aesthetics wise, and certainly not an improvement as to the location of the switch regarding ingress or heat.
  12. mainline

    Car headlight into house lamp

    Personally, I would sell it and buy a decent lamp and probably a nice meal :)
  13. mainline

    13amp outdoor ev charging socket

    What sort of earthing system have you ?
  14. mainline

    13amp outdoor ev charging socket

    That depends on how small the cable is :) :)
  15. mainline

    Retrofit Surge Protection Device & Other Matters

    Maybe I've word blindness or something, but I can't see a Hob, oven, or immersion are you on gas, oil?
  16. mainline

    Retrofit Surge Protection Device & Other Matters

    Yes, you are correct. But again, posting a pic of the cut-out/main fuse and CU would be helpful.
  17. mainline

    Retrofit Surge Protection Device & Other Matters

    Like already said a picture of the Cu would be a help. I would think that the best way is to have a Board change to something like a Fusebox spd/rcbo board. The cost of upgrading that CU + eicr maybe more than a new CU, and you will end up still having a plastic one.
  18. mainline

    Retrofit Surge Protection Device & Other Matters

    The Op did say that the board was populated with type AC mcbs. The Op in fairness did say he was getting an Electrician in he also said "my apologies if any of the above ramblings is talking tosh (I realise "a little knowledge is a dangerous thing").
  19. mainline

    Socket cracked and scoched from EV charger

    That type of plug and socket isn't designed to handle that sort of current for long periods of time. Mode 2 would probably be ok. No No
  20. mainline

    Socket cracked and scoched from EV charger

    722.55.101.0.201.1 Each AC charging point shall incorporate: (i) one socket-outlet complying with BS 1363-2 marked ‘EV’.