Does anyone know the max current rating of the above, im looking at the regs bearing in mind its clipped direct in no insulation of any kind above a false ceiling in T+E
Looking at the regs book page 282 reference ci know my general cable ampages ratings reference c clipped direct though all approxlike 1mm is 15 amps
1.5mm is 19 amps
2.5 is 27
4mm is 37
6mm is 47
and 10mm is 65
16mm is 87
and 25mm is 114
and thats off the top of my head, all others but thats cause i use those sizes of cable every day of my life
Different temp? Is it not this that is different in BRB and OSG because of the temp expressed? I dunno - havn't a copy of either!Looking at the regs book page 282 reference c 1mm 16A
1.5mm 20A
2.5mm 27A
4mm 37A
6mm 47A
10mm 64A
16mm 85A
A bit different to your figures
Nope same in both booksDifferent temp? Is it not this that is different in BRB and OSG because of the temp expressed? I dunno - havn't a copy of either!