EH????So long it follows the same route and of equal loadingJohn
Sorry Cables of equal size and follow the same routecan be fed off the Fuse/MCB
I see. You're wrong anyway. If you're doubling up cbales to feed the same device they should be the same size and follow the same route. If they are in the same MCB they can be whatever they want as long as they are within the CPD and circuit limits.
What would you put down for R1+R2
Measure all R1+R2's and write down the highest. You'd have to do the same with your way anyway.
Over the weekend I'll dig out the regs book and send the numbers over
Subject to installation method, grouping, and voltage drop, 1.5 sq. mm could be adequate on a 16A circuit. Mixed lighting/socket circuits wired in 1.5 on a 16A MCB are common on the Continent.You could put your sockets & pendants on the same breaker if you want - the only caveat being:1. you use a protective device low enough to protect the lighting cable.
2. you wire the whole lighting circuit in 2.5mm, with 20A wall switches, and a 16 or 20 A protective device
(alright, you`d be crackers to do either; but they`d comply........)
Applaud SmileyIt wouldn't be two circuits on one MCB by virtue of the fact that they are protected by the same MCB. This, by definition, makes it one circuit.
That's exactly what I said at the start.It wouldn't be two circuits on one MCB by virtue of the fact that they are protected by the same MCB. This, by definition, makes it one circuit.
wrong. conductors in parallel do not have to be same CSA. 433.4.2, also appendix 10I see. You're wrong anyway. If you're doubling up cbales to feed the same device they should be the same size and follow the same route. If they are in the same MCB they can be whatever they want as long as they are within the CPD and circuit limits.