Hi,

Been to look at a job at a Cattery. The customer wants a pathway lit from front of house round side to back of house. He wants approx 6 bulkhead fittings along the pathway but wants a pir either end to switch the lights on. How would this be wired up? Thanks

 
Hi,Been to look at a job at a Cattery. The customer wants a pathway lit from front of house round side to back of house. He wants approx 6 bulkhead fittings along the pathway but wants a pir either end to switch the lights on. How would this be wired up? Thanks
The switching part on almost every PIR I have seen is actually a small internal relay contact...

(You can normally hear them click when they physically switch on or off!)

{and you normally get the max switching load.. i.e. the current rating of the contacts}

Obviously they are a live contact that outputs 230v....

So all you are doing is wiring two switches to operate the same light or set of lights,

so that either can provide 230v for a set length of time (duration of the PIR) to illuminate the lights!

I have done Multiple PIRs onto lights several times..

Last one was 2 x PIR working 3 x Bulkheads...

e.g. 30x60watt lamps total load 180w switched by either of two PIRs rated at 500w max load...

Its no different than if you got a PIR to a lamp..

but also a manual switch to the same lamp...

either switch will put the light on..

but lights will only be off when Both switches are off!.

simples!

:Salute

 
Thanks for all the help from everyone above. I've got this job coming up so wanted to ask your opinions.

The bulkheads will be lighting up a pathway about a meter wide. It's L shaped 20 meters forward then 15 meters left which is a pathway around from business driveway to Cattery shed. It has a strong featheredge fence with concrete posts.

The plan was to replace existing adaptable box which is currently in corner of pathway with a bigger one then feed the pits either end with 4c swa then from adaptable box out to the bulkheads.

The customer wants the bulkheads either mounted on fenceposts (which I think will be difficult as they've got rebar in them and won't drill easily) I was planning on either mounting the bulkheads on the fence or making a wooden backboard up for the lights which would be stronger ?

Would you gland the swa into the bulkheads or into an adaptable box below then run flex to bulkheads ? How do you normally do this?

Thanks in advance for any help.

Matt :)

 