I need to install 3 x 6.5A heating mats.
I intend to use dedicated 20A radial in 2.5 mmT&E.
Thermostat can only switch 16A so I will use a contactor - 2.5mm in 2.5mm out
My question relates to the cable feeding the stat and in turn the contactor coil.
This will not need to be 2.5mm as the load of the coil is very small but as the entire circuit will be protected by a 20A MCB if I use a smaller cable will I have to fuse down this bit of the circuit or does the fact that the coil is a fixed load mean I can omit overload protection?