Good Evening
I have my 2391 Practical exam on Monday and a few concerns that Im hoping you can help me with
Test 1 - Visual inspection find x amount of faults.. im sure I will be OK with this one
Test 2 - 2 x Insulation Resistance tests... we are to do a complete test so am I right in saying it is main switch off but all MCBS switched on ??
The examiner then flicks a switch and puts a fault on the circuit - I guess the logical way to fault find is to knock off an MCB at a time and retest until by process of elimination you find the faulty circuit (however Im told it can be a N-E fault too) is how you would approach this test ?
Test 3- Earth Fault loop Impedance Im Ok with this 1
The its the full test which I aim to tackle in the following steps
1.Safe Isolation
2.Continuity of bonding and protective conductors
3.Polarity
4.Continuity of Ring Final Circuit Conductors
5.IR ( am I right in saying this will be main switch off and all MCB's off as im sure we have to test each circuit individually )
Im confident up to this point but from here I could do with some clarification so please correct me if im wrong but I think this is the order they want
6.Check supply polarity
If all OK is it time to power up ?
If so is it then
7.phase rotation
8.ZE
9.PEFC&PSCC
10.ZS
11.RCD
12.Functional Testing
I have my 2391 Practical exam on Monday and a few concerns that Im hoping you can help me with
Test 1 - Visual inspection find x amount of faults.. im sure I will be OK with this one
Test 2 - 2 x Insulation Resistance tests... we are to do a complete test so am I right in saying it is main switch off but all MCBS switched on ??
The examiner then flicks a switch and puts a fault on the circuit - I guess the logical way to fault find is to knock off an MCB at a time and retest until by process of elimination you find the faulty circuit (however Im told it can be a N-E fault too) is how you would approach this test ?
Test 3- Earth Fault loop Impedance Im Ok with this 1
The its the full test which I aim to tackle in the following steps
1.Safe Isolation
2.Continuity of bonding and protective conductors
3.Polarity
4.Continuity of Ring Final Circuit Conductors
5.IR ( am I right in saying this will be main switch off and all MCB's off as im sure we have to test each circuit individually )
Im confident up to this point but from here I could do with some clarification so please correct me if im wrong but I think this is the order they want
6.Check supply polarity
If all OK is it time to power up ?
If so is it then
7.phase rotation
8.ZE
9.PEFC&PSCC
10.ZS
11.RCD
12.Functional Testing