Hi everyone!
This is my first post so please be gentle!!
First of all, a general thank you to those of you who have posted replies in similar threads, it has been most helpful.
I now ask that the forces of greater minds and experience to unite and help little me in my quest to pass my 2391 practical exam next week!!
I managed to pass the written exam first time but unfortunately failed the first time round on the practical, something I hope not to repeat!
I have some experience, but not as much as many on this forum, so please have mercy on me. So here goes - I would appreciate some help with the general run down of the assement on the PIR (the first three tests on the assesment - faults/IR etc I am not worried about).
I have read some people saying as it is a PIR then the order of tests becomes somewhat irrelevant - is that true? What order is acceptable and the quickest in your opinions?
How would you space out the Schedule of test results with a three phase board feeding a single phase sub main? Leave a space, write SUB MAIN or similar and then fill out as normal?
Can I do IR test on the whole installation between phases (with dimmer switch on the sub main removed), between live conductors connected and earth, or do I test the Main and Sub main seperatley? (If yes for lives conected and earth, do I note this down on the schedule of test results, as there are boxes for live/live and live/earth for IR on the form.) I assume I would have to somehow have the contactor down on the motor starter and also flick any two way switches as I do the IR test.
What tests and how are they done on a FCU fed by MICC? (I haven't really worked with MICC so forgive me if that is a stupid question i.e - the tests are the same as for any radial circuit)
Should I be doing anything else with the starter motor circuit other than after safe isolation, link L1 and CPC of motor circuit at DB, measure between L1 and CPC at 3 phase socket outlet connected to load end of DOL starter, push in contactor of the DOL with insulated screwdriver to make the contact within the starter.
Repeat this using L2 and CPC and L3 and CPC, the highest reading becomes R1+R2 for the circuit.
The lighting circuit is wired in single core in metal conduit. I assume I check earth continuity by the r2 long lead method?
I am including a picture of a board which will be similar to the one I will be tested on, if there is anything else you think I should know, or general tips/advice please be my guest. I attended a 2391 practical training day which was very unhelpful, so hopefully I can get some real help here
Many thanks in advance, (if anyone could show me/send me an example of the schedule of test results written out for a setup like this I would be most grateful, as I have been told some conflicting methods!)
:Salute
This is my first post so please be gentle!!
First of all, a general thank you to those of you who have posted replies in similar threads, it has been most helpful.
I now ask that the forces of greater minds and experience to unite and help little me in my quest to pass my 2391 practical exam next week!!
I managed to pass the written exam first time but unfortunately failed the first time round on the practical, something I hope not to repeat!
I have some experience, but not as much as many on this forum, so please have mercy on me. So here goes - I would appreciate some help with the general run down of the assement on the PIR (the first three tests on the assesment - faults/IR etc I am not worried about).
I have read some people saying as it is a PIR then the order of tests becomes somewhat irrelevant - is that true? What order is acceptable and the quickest in your opinions?
How would you space out the Schedule of test results with a three phase board feeding a single phase sub main? Leave a space, write SUB MAIN or similar and then fill out as normal?
Can I do IR test on the whole installation between phases (with dimmer switch on the sub main removed), between live conductors connected and earth, or do I test the Main and Sub main seperatley? (If yes for lives conected and earth, do I note this down on the schedule of test results, as there are boxes for live/live and live/earth for IR on the form.) I assume I would have to somehow have the contactor down on the motor starter and also flick any two way switches as I do the IR test.
What tests and how are they done on a FCU fed by MICC? (I haven't really worked with MICC so forgive me if that is a stupid question i.e - the tests are the same as for any radial circuit)
Should I be doing anything else with the starter motor circuit other than after safe isolation, link L1 and CPC of motor circuit at DB, measure between L1 and CPC at 3 phase socket outlet connected to load end of DOL starter, push in contactor of the DOL with insulated screwdriver to make the contact within the starter.
Repeat this using L2 and CPC and L3 and CPC, the highest reading becomes R1+R2 for the circuit.
The lighting circuit is wired in single core in metal conduit. I assume I check earth continuity by the r2 long lead method?
I am including a picture of a board which will be similar to the one I will be tested on, if there is anything else you think I should know, or general tips/advice please be my guest. I attended a 2391 practical training day which was very unhelpful, so hopefully I can get some real help here
Many thanks in advance, (if anyone could show me/send me an example of the schedule of test results written out for a setup like this I would be most grateful, as I have been told some conflicting methods!)