I'm just getting back into 3 phase Installation after a twelve year break, could one of you kind chaps just confirm everything is as it should be with what I'm intending to do?

I have a diesel powered machine that has a conveyer either side of it (one to feed into the machine and one to take the product out) one motor is 8.5A and one is 5.5A 3 phase and earth, I believe these are to be wired via emergency stop etc by the company making the machine back to probably a 16A 3 pin+E plug.

The cable run is 45m and I intend to use 2.5mm 4 core swa that will be clipped to a girder around the building and out to a 16A 3P+E switched socket protected by a 16A type c mcb.

Thanks in advance.

 
there's a lot more to this than getting the right rating of supply.

Machinery directive for a start, and the first thing is a risk asessment to determine what category of emergency stop and guarding you need.

Best leave this to the machinery company, not an easy thing to just do as a one off.

 
there's a lot more to this than getting the right rating of supply.Machinery directive for a start, and the first thing is a risk asessment to determine what category of emergency stop and guarding you need.

Best leave this to the machinery company, not an easy thing to just do as a one off.
The machinery company will be doing all the wiring for the conveyers all I will be doing is providing them a socket to plug in to.

[quote name='Andy

 
No1.

You will get 20volts loss on 1.5mm cable at 45 meters. 2.5mm is more than adequate on a 20Amp breaker. Use C type breaker if using MCB.

Hope that helps

Also I have to add I noticed you said 4 core cable you were thinking...If the starter there using has a single phase contactor coil in you will need a neutral so you will need 5 core. If there using 400v coil then your good for a 4 core. :) Its always good practice when installing sockets, to use 5 core and provide a neutral for future use. Because whos to say someone might need that socket for something else??

 
Last edited by a moderator:
Your total load is 14A?
Yes, at least that is what I have been told, 1 motor is 8.5A and the other is 5.5A.

No1.You will get 20volts loss on 1.5mm cable at 45 meters. 2.5mm is more than adequate on a 20Amp breaker. Use C type breaker if using MCB.

Hope that helps

Also I have to add I noticed you said 4 core cable you were thinking...If the starter there using has a single phase contactor coil in you will need a neutral so you will need 5 core. If there using 400v coil then your good for a 4 core. :) Its always good practice when installing sockets, to use 5 core and provide a neutral for future use. Because whos to say someone might need that socket for something else??
Thanks for that, I will go for the 2.5mm 5 core.

Thank you to everyone who took the time to reply.

 
No1.You will get 20volts loss on 1.5mm cable at 45 meters. 2.5mm is more than adequate on a 20Amp breaker. Use C type breaker if using MCB.

Hope that helps

Also I have to add I noticed you said 4 core cable you were thinking...If the starter there using has a single phase contactor coil in you will need a neutral so you will need 5 core. If there using 400v coil then your good for a 4 core. :) Its always good practice when installing sockets, to use 5 core and provide a neutral for future use. Because whos to say someone might need that socket for something else??
5 Core ?????

SWA 4 Core, 3Ph + N, Armour = Earth.

 