Have a board change to do in a property with all cavity/gyproc walls. Was considering the 50mm depth rule for the ring circuit and wondered if the 30mA protection would be required here.
After looking in the BRB and double checking reg 522.6.6 & 522.6.7, i noticed 522.6.8 which more or less states that unless the installation is in a location supervised by skilled persons, you must always protect the circuit with 30mA RCD irregardless of the cable mounting depth, kinda contradicting.
Ive always been taught that if you cant prove the cable is mechanically protected or the depth of cables is more than 50mm, you should always install the RCD/RCBO to protect which i normally did, but thought that this occasion would be ok for standard RCD.
As most jobs dont warrant checking walls and cable depths etc does everybody just automatically use RCBO's or 30mA RCD's when connecting rings etc?
After looking in the BRB and double checking reg 522.6.6 & 522.6.7, i noticed 522.6.8 which more or less states that unless the installation is in a location supervised by skilled persons, you must always protect the circuit with 30mA RCD irregardless of the cable mounting depth, kinda contradicting.
Ive always been taught that if you cant prove the cable is mechanically protected or the depth of cables is more than 50mm, you should always install the RCD/RCBO to protect which i normally did, but thought that this occasion would be ok for standard RCD.
As most jobs dont warrant checking walls and cable depths etc does everybody just automatically use RCBO's or 30mA RCD's when connecting rings etc?