OK, can you or can you not spur of a lighting loop to supply a FSO to a combi boiler

Just one of those silly debates you find yourself in

 
Yes ,theres no reason why not . A combi usually has a 3 amp fuse. A lot of sparks will have a problem with this , and obviously its not the best way of doing it but no different to the timed extract fan really.

Deke

 
I have to agree , I have when limitations have been in place taken a supply to a boiler from the local lighting circuit.

Normally I like to have a dedicated boiler supply but not always practicable.

 
I have to agree , I have when limitations have been in place taken a supply to a boiler from the local lighting circuit.Normally I like to have a dedicated boiler supply but not always practicable.
as hornet says i like a dedicated supply but not always practical

 