Hi,
I had a new 14 panel (approx 5.6KW) system installed last December with a Growatt SPH5000 inverter, no batteries by an "award winning" installer.
Two inverters have failed, both due to power cuts and I am now organising a third replacement with the company. I suspect there might be an underlying fault in the install or with this model of inverter that means a 4th replacement isn't too far away, but I have no idea what that would be? Nothing else in the house blows up, and neighbours solar inverters have survived the same power cuts for years.
A bit of background first on this troublesome install:
Company is coming out next Thurs, hopefully to fully replace but that's not entirely certain at this point, they like to drag things out. Should I be asking them to check some other parts of the install before sacrificing another inverter?
Any advice and thoughts welcome.
Thanks, Matt.
I had a new 14 panel (approx 5.6KW) system installed last December with a Growatt SPH5000 inverter, no batteries by an "award winning" installer.
Two inverters have failed, both due to power cuts and I am now organising a third replacement with the company. I suspect there might be an underlying fault in the install or with this model of inverter that means a 4th replacement isn't too far away, but I have no idea what that would be? Nothing else in the house blows up, and neighbours solar inverters have survived the same power cuts for years.
A bit of background first on this troublesome install:
- Installed and "commissioned" in the dark in December, next day when sun hit the panels tripped out with PV High warning
- Turns out they should have split into two strings as the single string voltage exceeded the max DC voltage.
- After many delays, cancellations they sent a "roofer" in February to restring the panels who had to borrow my crimping tools (no, not proper MC4 ones), he also told me there was no electricity in the DC/Solar cables, it was just data!
- Had to assist the confused roofer with my own multi-meter and neither string worked. More delays, the electrician arrives and discovered the polarity had been reversed, swapped - working system at last!
- One month later in March, power cut, inverter stops working, Growatt remote in and confirm fault. Protracted return via Growatt before a replacement install in April. Assumed the old inverter had been compromised by the previous miswiring in some way.
- Working great for 4 months, exporting to Octopus, using home assistant to monitor etc... Until today - Short power cut, inverter completely dies, even the display is dead, no remote diagnosis on that!
Company is coming out next Thurs, hopefully to fully replace but that's not entirely certain at this point, they like to drag things out. Should I be asking them to check some other parts of the install before sacrificing another inverter?
Any advice and thoughts welcome.
Thanks, Matt.