- Dec 25, 2011
- 5,468
- 78
Is it the case that 6mm T&E from a while back would have had the same size CPC as the L & N conductors? All I know is that the cable is pre 1987. Basically I've fitted a new induction hob and as I can't physically get to the cable to check along it's length I tested it - I would have anyway but have had rat issues. It will be replaced eventually but I have to go with it for now. I've no exact length (guessing circa 12m) either but that can be calculated I know. Any comments appreciated.
Results as follows:
For continuity using the long lead "Method 2" I first checked the cpc. Accounting for the long lead resistance I got 0.04ohms end to end. Same for the L & the N. For R1+R2 I then connected the CPC and L at the CU with a connector block and tested at the CCU getting 0.08ohms. Says to me that the cpc is the same size. I know someone's going to say "vernier" but my digital one is playing silly beggars).
On a TT BTW.
IR was >999Mohms between all 3 conductors
Zs at the CCU was L/PE, 35A/6.5ohms then L/N 623A/0.37ohms
Ze (Zd according to my manual)with the main earth disconnected was L/N 0.31ohms/745A then L/PE 79.3ohms/3A
RCD 30mA: x1/2, no trip / 0deg 26.8ms / 180deg 36.2ms / x5 0deg 7.5ms / x5 180deg 12.6ms / Ramp 24.2ms
Results as follows:
On a TT BTW.