Hi All
Wonder if anybody can give some advice
I tried to do a RCD test - with a Multifunction tester - Seaward Powertest 1557 on my house
It done the half test no problem
Tripped straight away on x1 but displayed "RCD" on the screen and would not give a time
Tripped straight away on x5 and displayed "RCD " on the screen again and would not give a time
The button on the RCD unit is working and tripping it
Tried to do a loop test - the tester would not as it said the fault current would be over 50volts
After an age I narrowed it down to the Down stair ring circuit it had a Live to Earth fault when I tested the Insulation Resistance
I replaced the cable between the 2 sockets concerned - HAPPY DAYS - or so I thought !!
Decided to test the whole lot again from scratch
Disconnected the Main Earth in the CU to do a Ze test 0.20 ohms - It is a TNCS supply
Just happened to probe between main disconnected Earth and the Earth bar in the CU I got 80 volts !!!
The 80volts reduces as you switch the circuts off but NO circuit in particular stops it
The CU was a total mess and Was not Identified so I stripped it all out so I could make sure everything was where it should be
I have now stripped the board wiring out and tested all the circuts seperatly they all passed IR and R1+R2
But the 80volts is still there
And now the RCD will NOT trip on x1 or x5 and is displaying more than 300ms for the x1 and more than 40ms on the x5 and will not ramp test BUT the RCD test button will still trip it if pressed
Im going to now start testing between the Earth & Neutral on each circuit as I only done the end to end and the R1+R2
Has anybody ever come across this before ????
Is it possible to check the supply cable to see if it has a broken Neutral or Earth coming in _ just so I can rule that out ??
They are putting up a housing estate across the road and Im wondering if they could of damaged the cable some how
Ant help or thoughts welcome
Wonder if anybody can give some advice
I tried to do a RCD test - with a Multifunction tester - Seaward Powertest 1557 on my house
It done the half test no problem
Tripped straight away on x1 but displayed "RCD" on the screen and would not give a time
Tripped straight away on x5 and displayed "RCD " on the screen again and would not give a time
The button on the RCD unit is working and tripping it
Tried to do a loop test - the tester would not as it said the fault current would be over 50volts
After an age I narrowed it down to the Down stair ring circuit it had a Live to Earth fault when I tested the Insulation Resistance
I replaced the cable between the 2 sockets concerned - HAPPY DAYS - or so I thought !!
Decided to test the whole lot again from scratch
Disconnected the Main Earth in the CU to do a Ze test 0.20 ohms - It is a TNCS supply
Just happened to probe between main disconnected Earth and the Earth bar in the CU I got 80 volts !!!
The 80volts reduces as you switch the circuts off but NO circuit in particular stops it
The CU was a total mess and Was not Identified so I stripped it all out so I could make sure everything was where it should be
I have now stripped the board wiring out and tested all the circuts seperatly they all passed IR and R1+R2
But the 80volts is still there
And now the RCD will NOT trip on x1 or x5 and is displaying more than 300ms for the x1 and more than 40ms on the x5 and will not ramp test BUT the RCD test button will still trip it if pressed
Im going to now start testing between the Earth & Neutral on each circuit as I only done the end to end and the R1+R2
Has anybody ever come across this before ????
Is it possible to check the supply cable to see if it has a broken Neutral or Earth coming in _ just so I can rule that out ??
They are putting up a housing estate across the road and Im wondering if they could of damaged the cable some how
Ant help or thoughts welcome