Hi all, First off, i would have thought by now that everyone would have got used to the idea that it is PERFECTLY ACCEPTABLE to export PME earths. No good arguing with me, take it up with the IEE or the electrical safety council if you disagree, it is their considered opinion not mine!!!!Anyway, Plumber is exactly right; just because the CSA of a SWA cable meets the THERMAL constraints that allow it to be used as a cpc, does not mean that it meets the conductivity requirements to be equivalent to a 10mm copper conductor that would be required for a PME bond. [That is, assuming your incoming supply neutral is 35mm or less] To do this would require an armouring CSA of about 80mm, so you would be looking at a very large cable!!
Further, as Plumber also points out, there are other issues involved with using the armour [or an internal core] of a cable as a PME bond. This is because of the extra heating effect of such use on the cable concerned. You CAN use an internal core or the armour [if the CSA is large enough] PROVIDED the cable is only lightly loaded, This is where your judgement comes in!!! What would you call "lightly loaded" Personally, and this is only me [and I have not passed my 17th ed yet!] i would have thought that as the heat in a cable is a function of the current squared, that calculating the current that gives out say, half the heat of a fully loaded cable, [and no, this is not just a question of halfing the original current!] one would produce a cable that would count as "lightly loaded" As i say though, this is just the way i see things, others may take a different view!!!!!
In the event that the armour is not of a sufficient CSA to act as the bonding conductor, you are not allowed to "top it up" as it were by adding a separate smaller cable in parallel. Obviously, any separate cable you do add will be in parallel to the armour, but, the additional cable MUST of itself be large enough to act as the bonding conductor on its own, without any help from the armour. This is because due to various magnetic effects, the like of which are beyond me, it is impossible to predict how the fault current would be shared between the two [not just a case of Ohms law apparently]
Finally the size of bond required in a PME system is determined by the size of the incoming neutral of the supply. That does not mean the size of the conductor in your swa, or the size of you meter tails either, but the size of the neutral in your service cable..
Hope all this helps or is at least interesting!!
john..