Description No. of points served Connected Load per point Total Connected Load Of All Points Allowance For Diversity (From Table 3) Resulting Contribution To Maximum Instalation Demand (in amps) LED Square Fittings 15 38w 2.64 amps 90% 2.4 2d stair fittings 2 28w 56/230= 0.2 amps 90% 0.18 LED spot lights 5 12.5w 62.5/230= 0.27 90% 0.24 32a ring (floor) 10 see note 1 32 A 100% of current demand of largest circuit plus 50% of current demand of every other circuit 32 32a ring (floor) 10 see note 1 32 A 17 323a ring (wall) 8 see note 1 32 A 17 16a radial (below D/B) 1 see note 1 16 A 8 Heating/air con 1 32 A 32 A 100% of largest circuit plus 75% of F.L of the remaining Circuits 32 Meeting room Heating/Air con 1 16 amps 16 amps 12 120.82
This is the total demand i worked out using guidance note 1. and NIC guidlines. Obviously its high.. what obvious thing am i missing?
the electrician who wired the original office which has twice as many circuits and twice as many heaters/air con units, put the maximum demand as just 60amps what am i missing?
is there leway for me to just decide how many amps are going to be used on each circuit? so instead of putting 32 amps id put say 15 amps for 6 work stations?
I would guess you have failed to fully ready paragraph 2 of appendix H guidance Note 1....
says something like information is intended as guidance because it is IMPOSSIBLE to specify diversity allowance for every type of installation...
Such allowance call for specialist knowledge & experience...
Figures in tables may therefor be increased or decreased as decide by competent person responsible for design...
etc..
ect...
in a nut shell you cannot simply add up MCB ratings and/or use percentages of MCB ratings to calculate max demand...
It is knowledge of the installation and how it is going to be used that is needed...
e.g.
I could split a 32A ring into 2x 20A radials..
that doesn't suddenly make the max demand go up by 8Amps...
The loading could well stay the same but it is just more convenient if one MCB trips!!!
IMHO the rule of thumb figures in the tables are only any use for the simplest of CU's..
such as 4 or 6way small domestic installation
Consider two identical properties... same fuse box and final circuits..
one has two elderly persons age 80+ very little power useage..
The other has family of 8.. couple with 6 children aged between 5 and 19..
much more power used...
Calculating MCB ratings would be a waste of time and incorrect!!!
You are going to have to use your knowledge of the installation to make a judgment call and sign off for your design on the electrical certifiacte....
If you are not confident to do that best get some help..
it is almost impossible for anyone on here to accurately calculate anything as we don't know the site!