Good evening,
I am heading down the path of a DIY solar install in a bid to avoid the energy price hike coming when my current deal ends!. I am hoping a kind and informed soul may be happy to share some advice regarding my setup as I want to ensure the build is safe!.
My house / garage suffers from shading issues due to trees and a neighbouring property. I intend to install my setup on a ground mounted frame in a small fenced field at the rear of my house. This location has no issues at all with shading.
I have purchased 10x540w JA Solar panels
(datasheet)
https://cdn.shopify.com/s/files/1/0...0-555_MR_Global_EN_20210531A.pdf?v=1668948978
and a Solis 6kW Hybrid 5G Energy Storage Inverter
(datasheet)
https://cdn.shopify.com/s/files/1/0...-af06-4462-b7f5-ca727b726840.pdf?v=1675337102
If my interpretation of the datasheets is correct, wiring these panels in series should allow me to run about 500v DC and 13amps in optimum conditions. I realise the average output will be considerably less but I want to ensure the system can meet optimal requirements.
I intend to install the inverter and battery setup in the garage which is about 120 meters from the panels. With this in mind my query is regarding DC cable size and ducting. Will 6mm2 solar DC cable in a ducting be sufficient over this 120m run? If so, is non perforated twin wall land drainage ducting, say 50mm, suitable for such a setup? lastly, assuming this is suitable, is there any recommended depths for the burial of such ducting/cable.
I am aware of the need to seek the approval of the DNO given the solar capacity and want to ensure the basic install approaches industry standards, even if installed by an enthusiastic beginner!
Many thanks for your help.
BV
I am heading down the path of a DIY solar install in a bid to avoid the energy price hike coming when my current deal ends!. I am hoping a kind and informed soul may be happy to share some advice regarding my setup as I want to ensure the build is safe!.
My house / garage suffers from shading issues due to trees and a neighbouring property. I intend to install my setup on a ground mounted frame in a small fenced field at the rear of my house. This location has no issues at all with shading.
I have purchased 10x540w JA Solar panels
(datasheet)
https://cdn.shopify.com/s/files/1/0...0-555_MR_Global_EN_20210531A.pdf?v=1668948978
and a Solis 6kW Hybrid 5G Energy Storage Inverter
(datasheet)
https://cdn.shopify.com/s/files/1/0...-af06-4462-b7f5-ca727b726840.pdf?v=1675337102
If my interpretation of the datasheets is correct, wiring these panels in series should allow me to run about 500v DC and 13amps in optimum conditions. I realise the average output will be considerably less but I want to ensure the system can meet optimal requirements.
I intend to install the inverter and battery setup in the garage which is about 120 meters from the panels. With this in mind my query is regarding DC cable size and ducting. Will 6mm2 solar DC cable in a ducting be sufficient over this 120m run? If so, is non perforated twin wall land drainage ducting, say 50mm, suitable for such a setup? lastly, assuming this is suitable, is there any recommended depths for the burial of such ducting/cable.
I am aware of the need to seek the approval of the DNO given the solar capacity and want to ensure the basic install approaches industry standards, even if installed by an enthusiastic beginner!
Many thanks for your help.