redman
Member
Hi all,
Ive just done an electrical inspection & test on my own house.
Ive not had any problems with the electrics over the past 3 years that i`ve lived here.
I`ve done it, mainly to get some testing practice, also just to see if it complies with the current regs.
The consumer unit has a sticker saying it was changed in 2004 & has RCD protection on everything apart from the lights.
Most of the test results are good, its just 2 circuits that are a bit dodgy.
1st circuit -
Lighting - 1.0mm t&e - B6 MCB
R1+R2 = 1.53 ohms
Ins Res: L/N = >200 M ohms
L/E = > 200 M ohms
N/E = 25 M ohms
Zs = 1.68 ohms
Although these results are within the figures from the on site guide, I still think there is an issue with the neutral / earth insulation resistance test. But because this circuit is not on an RCD, nothing has ever tripped.
Then the 2nd circuit -
kitchen Ring - 2.5mm t&e - B32 MCB
r 1 = 0.17
r 2 = open circuit
r n = 0.18
R1 + R2 = 0.26
Ins Res: L/N = >200 M ohms
L/E = 8 M ohms
N/E = > 200 M ohms
Zs = 0.36 ohms
RCD: X1 = 98ms
X5 = 23ms
I think this just appears to have a break in the CPC somewhere on the ring.
Ive checked all the socket connections & they look ok.
The cables are under floorboards or on the wall, burried in plaster. So ive not been able to visualy check the cable route.
So..... what would you guys do now in this situation, regarding these 2 circuits ?
Any advice welcome,
Cheers
Ive just done an electrical inspection & test on my own house.
Ive not had any problems with the electrics over the past 3 years that i`ve lived here.
I`ve done it, mainly to get some testing practice, also just to see if it complies with the current regs.
The consumer unit has a sticker saying it was changed in 2004 & has RCD protection on everything apart from the lights.
Most of the test results are good, its just 2 circuits that are a bit dodgy.
1st circuit -
Lighting - 1.0mm t&e - B6 MCB
R1+R2 = 1.53 ohms
Ins Res: L/N = >200 M ohms
L/E = > 200 M ohms
N/E = 25 M ohms
Zs = 1.68 ohms
Although these results are within the figures from the on site guide, I still think there is an issue with the neutral / earth insulation resistance test. But because this circuit is not on an RCD, nothing has ever tripped.
Then the 2nd circuit -
kitchen Ring - 2.5mm t&e - B32 MCB
r 1 = 0.17
r 2 = open circuit
r n = 0.18
R1 + R2 = 0.26
Ins Res: L/N = >200 M ohms
L/E = 8 M ohms
N/E = > 200 M ohms
Zs = 0.36 ohms
RCD: X1 = 98ms
X5 = 23ms
I think this just appears to have a break in the CPC somewhere on the ring.
Ive checked all the socket connections & they look ok.
The cables are under floorboards or on the wall, burried in plaster. So ive not been able to visualy check the cable route.
So..... what would you guys do now in this situation, regarding these 2 circuits ?
Any advice welcome,
Cheers