Aircon pipes spanner size
Status
Not open for further replies.
I'm in the UK
Electriq spec says:
"Contains everything you need for installation, does not require installation by an F-Gas registered engineer or specialist equipment"
I'm in the UK
Electriq spec says:
They run on R290 which is propane based, not a greenhouse gas.
The aircon is installed and running.
I shortened the outside copper pipes and flared the ends with a £15 brake pipe flaring kit.
Used Nylog on the flares.
As someone predicted earlier, the compression joints were four different spanner sizes from 15mm up to 20mm.
That's on two 1/4" pipe joins and two 3/8" pipe joins.
No torque wrench, just spanners.
Standard wiring would be an unsightly 13A plug and cable from the indoor unit down the inside wall to a 13A socket outlet.
Instead I extended the mains cable and bundled it with the pipework to a IP rated switch adjacent to the external unit.
All the external pipework in white 110mm x 75mm duct.
Forgot to mention.
The aircon can only be operated with the remote control.
The buttons on the supplied remote were different to the image in the User Manual.
I sent images of both to the Help Line.
They sent four different PDF manuals, none of which matched my remote - useless.
Finally admitted they were working on a new manual for the latest remote that I have.
No time frame offered.
4 months on I can report that the unit has lost it's refrigerant !
Probably a connection not torqued correctly.......... ?? !!
I decided to get it pressure tested , fixed, and refilled, but have been given the runaround by local aircon engineers.
So I will fill it with nitrogen, test for leaks, and refill with 400g of R290 myself, and hope for the best.
My question is:
Does the aircon compressor have it's own oil supply, does the Refill have oil in it, or do I have to add an unknown quantity of mineral oil myself ?
Evacuated with the pump and left it with the pump off.
Nothing lost after an hour, but pressure was halfway back to ambient the next morning.
A visual inspection of all the connections showed no signs of lost refrigerant - would there be any signs ?
Awaiting the arrival of the consumables.
Repaired and working again.
Found a YouTube of a refill of my particular ElectriQ unit. Didn't agree with everything he did but it was helpful:
I bought a canister of nitrogen to pressure test.
The canister has a 10mm connection. Finding a tap with 10mm to 1/4" SAE flare connections proved impossible. Most seem to be 11mm, listings of 10mm taps had no details of the output connections, and nobody would reply to requests for details.
In the end I screwed a 1/4" SAE flare connection into a CO2 gas regulator I had that happened to have a 10mm input.
The pressure test using a can of Leak Detector revealed a leak on one of the connections directly onto the outside unit. A slight tightening with spanner stopped the leak and the aircon held pressure overnight :->
The 1/4" Male to 5/16" adapter for the aircon charging port that I had used when first installing started leaking at the 1/4" end. This was the type with a slightly bent section of thin steel tube between the two connectors. I bought a replacement that was a short solid brass item with the connectors at each end, no pipe, no leaks.
I bought a 370g canister of R290, and a tap with 1/4" SAE flare output. Didn't get anywhere near 370g of R290 out of it, according to the kitchen scales. So I warmed the canister up by immersing it in a jug of hot water when it was nearing empty, to increase the gas pressure .
Don't do that to a canister that isn't connected to the aircon, the increased pressure must have somewhere to go !
That way I got 300g out of the canister, so topped up with a second canister of R290 to 400g total.
Good update
Air con finished, thread now locked
(If you have an air con question, please start a new thread.)
Status
