I bet you can work it out.C'mon Dave the suspense is killing. I cant work it out but defo think the split load wiring inside the cu is incorrect
nothing to be laffed at John,Hmmm, let me try beginners luck again!! [i must be mad!!] You isolated the house at the CU. This is a DP switch/disconnector, that presumably worked. You said you did not do a "proper" deadness [for want of a better word] check, but everything went off.Now then, it appears that the CPC was still live.......Hmmmm..... well.... if the CPC is live, then the earth bar in the CU must be live too. The earth bar is connected to the MET, so that must have been live too, and that is connected to the neutral [as it is pme]
Sooooo, how is it live???
Either the earthing conductor was not [conducting that is!!] and the MET was bonded to an incoming service that was live some how,
or,
The MET was not bonded to "earthy" incoming services, [all plastic in a newish house] and the neutral that the MET is connected to ij the cutout [cos its pme] was not as "neutral" as one would like!!
Soooooo, something wrong with the incoming PME but the house holder did not notice as, well, he would not if all the metalwork was bonded to the MET as it would all be the same potential. [unless he went out side with his ancient class one black and decker!!]
All i can think of!!
Do not all laugh at once!!!!!!!!!!!!!!!!
john
Nope. CPC is at earth potential (linked to neutral at PME supply head). Try again.
No, CPC was not live, well and truly at earth potential direct from the PME head.Now then, it appears that the CPC was still live.......Hmmmm..... well.... if the CPC is live, then the earth bar in the CU must be live too. The earth bar is connected to the MET, so that must have been live too, and that is connected to the neutral [as it is pme]
I'm beginning to think along those lines, Steps, because if the 'main switch' isn't faulty, or by-passed, then the only 'potential' that could exist is on the MET via the PME supply - but then you still need to complete the circuit.nothing to be laffed at John,its got you thinking,
Im not even going to say its one of the limitations of why I regard PME(in this country) as defective, as we have already seen, TT has its limitations too.
Actually this fault has nothing to do with PME and in this case the PME supply was not defective.Im not even going to say its one of the limitations of why I regard PME(in this country) as defective, as we have already seen,
CPC is correctly bonded to neutral at the PME supply head, and bonded to water / gas as it should be, so it's 0V relative to what it should be. The fault did not relate in any way to a defective supply or defective earthing.CPC at 0 volts relative to what??
No.No extra funny feeds from solar panels??