Right. Imagine a ring final circuit all wired in 2.5mm twin and earth.
Now if you need to spur from this circuit you can do so. Providing you wire from the chosen socket to your spurred socket/fused spur in 2.5mm twin and earth. Correct?
So if you find within a distribution board in a ring final circuit 32amp rated mcb, along with the two cables for the ring in there, there is also another 2.5 twin and earth cable. Turns out its supplying the boiler. From the board to the boiler in 2.5mm where it is then connected into a 3A fused spur and the boiler is then fed from that etc etc.
So in theory that boiler is spurred from the ring. Its not spurred from a j.b or back of a nearby socket but from the consumer unit. But its still a spur.
Nothing wrong with that so far?
So is this deemed ok by the majority here? Only what happens should a fault develop? Isnt 2.5 only suppose to take 20 odd amps before getting a little hot? But theres a 32amp breaker protecting it, not a 16 or 20?! The ring would be fine but what about the single 2.5mm cable?
So if you come across a situation like this where theres no room in a consumer unit to wire the new boiler on its own dedicated 16A circuit and some mush has wired it in with the ring? Isnt it technically just a spur and safe? Or potentially dangerous?
Or have I had too much Stella for a Sunday night.
Discuss.
Now if you need to spur from this circuit you can do so. Providing you wire from the chosen socket to your spurred socket/fused spur in 2.5mm twin and earth. Correct?
So if you find within a distribution board in a ring final circuit 32amp rated mcb, along with the two cables for the ring in there, there is also another 2.5 twin and earth cable. Turns out its supplying the boiler. From the board to the boiler in 2.5mm where it is then connected into a 3A fused spur and the boiler is then fed from that etc etc.
So in theory that boiler is spurred from the ring. Its not spurred from a j.b or back of a nearby socket but from the consumer unit. But its still a spur.
Nothing wrong with that so far?
So is this deemed ok by the majority here? Only what happens should a fault develop? Isnt 2.5 only suppose to take 20 odd amps before getting a little hot? But theres a 32amp breaker protecting it, not a 16 or 20?! The ring would be fine but what about the single 2.5mm cable?
So if you come across a situation like this where theres no room in a consumer unit to wire the new boiler on its own dedicated 16A circuit and some mush has wired it in with the ring? Isnt it technically just a spur and safe? Or potentially dangerous?
Or have I had too much Stella for a Sunday night.
Discuss.