433 is the chapter which covers most of the above points AFAIK?
433.2.2 does say... the overload protection device may be fitted ALONG the run of the cable,
providing the cable has no branches or outlets
and should be no longer than 3m.
but 434.2 does prefer protection to be at point of change in C.S.A size.
433.2.2 does say... the overload protection device may be fitted ALONG the run of the cable,
providing the cable has no branches or outlets
and should be no longer than 3m.
but 434.2 does prefer protection to be at point of change in C.S.A size.