I was asked by a former client who I have done some commercial work for to check out a first fix that another electrician had carried out in a house they had bought.

The first question they asked me was about having a junction box on a full rewire, I informed them that it was not usual on a rewire but not against any regulation. They then asked why would you have spurs off the ring main, again I said it would be unusual but without knowing why I could not comment.

Anyway I went along to the house and found some very peculiar wiring techniques.

At the CU the cables are marked and has been wired in a mixture of singles and twin &earth, the lighting has been wired in twin brown and earth, with two nuetral singles. On testing I found continuity up to two of the bedrooms but none to any lights other than them. They have wired most of the feeds to the switches, yet looped some of the neutrals.

Anyway we had to cut a hole in the ceiling below the bathroom which now has a new tiled floor. On inspection of the connections it looks like he has tried to seperate the lighting circuits by using the twin brown, so that one bron feeds one circuit and the other feeding the other, only problem is that all the lives once connected will be shared and because there is only one earth cable there will be no way the lighting can test out.

The electrician now says that its ok to use twin brown providing they are identified, I agree but that is only if its a neutral not two seperate feeds.

My question is how the hell is this lighting circuit going to be wired? Did he expect to seperate the browns on to two seperate mcb's and RCD's?

The customer is now very reluctant to have this guy do anything else, I do not blame them, I have told them that if I was to sort it out for them I would have to rewire the whole lighting circuit, plus get rid of the spurs.

Forgot to mention it has now been fully plastered.

 
Wow how can anybody get something so easy so wrong.
Its so difficult trying to explain in words I will go back and get some pics they will speak volumes.

On another note I believe they have reported him to his governing body, who have so far been very unhelpfull.

Its not NICEIC thats all I can say.

 
Its so difficult trying to explain in words I will go back and get some pics they will speak volumes.On another note I believe they have reported him to his governing body, who have so far been very unhelpfull.

Its not NICEIC thats all I can say.
Makes a change then.

 
Wow how can anybody get something so easy so wrong.
Sounds like he over thought it and tried to use only the materials he had in stock :yellow card

 
can you run multiple feeds in a multi core?

i.e as you say 2 mcb's 1 for each brown!

surely only if the mcb's are double pole/jointed but then you'd breach another reg

 
The single neutrals are the sleeved type often used in the past but rare these days.

The problem with the twin brown and earth is that they are both live, and sharing 1 1.00mm earth. So on one side we get continuity, the other side we do not. The fun does not start end there though, failing to find any common route I energised each brown in turn, and found that both lives will energise all lighting with exception of the bathroom which has its own twin and earth. So even though there are seperate neutrals the lives are interconnected. I have some live feeds at the switches and some at the point of fixing, I even have a seperate dimmer live feed, I never knew dimmers needed its own live feed.

Its a mess, I found out after some discussion that this same electrician could not get a two way switch to work, and told the old lady that she would have to use the switch at the bottom of the stairs. OMG.

 
the governing bodies are never interested unless there is some money involved !

i have tried calling them quite a few times over concerns with other peoples dangerous installs .

 
I wouldn't be supprised if he wired the lighting in and only then realised he had done it in twin brown.

 