assuming 30mA RCD, max Zs is 1667 ohms.Hiya guys, on a TT system I keep getting a very high ZS reading,ze = 33.1ohms
PFC = 1.8 KA
All r1+r2 reading are good but my Zs reading on all circuits are all coming out at 16.4 - 17.2 ohms.........
Any suggestions ?
Sorry, don't really know what you're on about here..There is 16 circuits and 6 of them are over 32amps ...... all circuits are protected by 30ma RCDs so are ok but what about the circuits that are over 32Amps?????
Yes I do understand what you guys are saying, just that in Table 41.5 its say Max earth loop impedance (Zs) to ensure RCD operattion in accordance with regulation 411.5.3 for non delayed RCDs to BS EN61008-1 and BS EN 61009-1 for Final circuits not Exceeding 32A ? I'm just not understanding this Bit?????rob196. You seem to be posing two seperate questions here. Presumably you now realise the reasoning behind your Zs readings...so thats question one out of the way. ...You now appear in your second question to be in doubt as the suitability of a 30mA RCd installed as protection on the circuits rated above 32A.You need to clarify why you are concerned in this respect. Obviously the term 30mA is referring to the value of leakage current the RCD is designed to operate at [max value].Not its rated loading value, or are you concerned over the number of circuits installed on the RCDs...if so then Diversity is the answer to your question........more input required here rob.
Theoretically for a maximum disconnection time of 1 sec you would need a fault current of 30mA because the RCD should trip out in ≤ 300mS at it's operating current.Therefore your theoretical max Zs on circuits over 32A is 7666.66Ω
230
Yes you could. I was just using 30mA as an example as they are the most common.JUD ,would not a 100mA RCD [ or even higher ] still be acceptable in a TT install for circuits greater than 32A which are not in a Special location ?I think this is why table 41.5 is not appropriate in the OPs question.
Appendix 3. Table 3A.