Existing workshop with no bonding .
Supply is an SWA possibly 50mm sq or 70mm X 4 core TPN to a 200A Sw/fuse I can only guess the size by looking .
According to Table 54.8 the bonding needs to be 25mm .............BUT .......... the origin of the supply is a BBC 40 mtrs away with the metering and 3 X 100A service fuses with 25mm tails .
My question is , should I size the bonding to the 25mm tails or the 50 / 70mm SWA sub - main which is for the volt drop I imagine. The 200A Sw/Fuse must be for the physical size :C Can't switch off to look at the fuses , not that it matters much as the service is 100A .