Okay. Commercial premises being rewired from scratch.
A series of 5 interconnected sheds. Existing was one DNO supply point, subbed to all 5 sheds - but we`re having our own TN-C-S installed.
All OUR water is alcathene; however; the water service enters the first shed in copper, and runs all the way to the end shed - feeding everyone along the way.
The pipe is installed at roof height - 6.5 metres - along the steel girder forming the front of the building.
Our plumber has teed into the pipe, and brought out alcathene to all our services.
We`re bonding the structural steel anyway - but I need to justify installing a 50mm ( or maybe 75mm) main bonding conductor across the whole length of the building - 50 metres.
On the one hand - the water service is IN our building - but inaccessible ( effectively) ; but on the other, the client sees our water service as plastic.
OR - would you deviate, and bond the copperwork to the structural steel adjacent to it?
Discuss???
A series of 5 interconnected sheds. Existing was one DNO supply point, subbed to all 5 sheds - but we`re having our own TN-C-S installed.
All OUR water is alcathene; however; the water service enters the first shed in copper, and runs all the way to the end shed - feeding everyone along the way.
The pipe is installed at roof height - 6.5 metres - along the steel girder forming the front of the building.
Our plumber has teed into the pipe, and brought out alcathene to all our services.
We`re bonding the structural steel anyway - but I need to justify installing a 50mm ( or maybe 75mm) main bonding conductor across the whole length of the building - 50 metres.
On the one hand - the water service is IN our building - but inaccessible ( effectively) ; but on the other, the client sees our water service as plastic.
OR - would you deviate, and bond the copperwork to the structural steel adjacent to it?
Discuss???