Hi all,Now, i am not getting involved in arguments with people with a LOT more knowledge than I. So, i will merely confine myself to making an observation [or two!!]
First off, every installation has only ONE origin, secondly, every installation has only ONE MET..
Where you have an installation split into several "components" shall we say, [you know what i mean!!] fed by a series of submains, this does not change things, you still have the one MET, you still have the one earthing conductor. Everything after the MET is a CPC.
All the other "MET's" are in fact "BEMT's"
Now look at this from the point of view of the DNO.... You go to a particular flat, and measure Zs or Zdb if you like and say it is 1.2 ohms.
It is no good then, phoning the DNO and saying the Ze for my flat is too high.
They will come along, test Ze at the origin [their cutout] pronounce it ok, and tell you that the rest of the wiring belongs to you [not them] and so it is part of YOUR installation not theirs. They will just say their Ze is ok, and suggest to you that if Zs in your flat is too high, that you get yourself a lower impedance submain, or TT the lot....