MCS installation instructions for solar pv(MIS3002) refer to the department of trade and industry best practice guide, in the current version of the guide it states:
An inverter supplied from a PV array must preferably be installed in a
dedicated circuit in which:
no current-using equipment is connected, and
no provision is made for the connection of current-using equipment,
and
no socket-outlets are permitted.
An inverter must not be connected by means of a plug with contacts
which may be live when exposed.
Where an electrical installation includes a PV power supply system
without at least simple separation between the a.c. side and the d.c.
side, an RCD installed to provide fault protection by automatic
disconnection of supply must be type B RCD according to BS EN 60898
(IEC 60755, amendment 2).
a.c. cables are to be specified and installed in accordance with BS 7671
So in order to comply with this and BS7671s requirements it would be very hard to comply on a pre existing cable
Should be noted that the draft update to the DTI guide if it passes in its current form no longer uses the word preferably and has been changed to should.
Looked further into MIS3002 and found on page 8:
Furthermore an inverter supplied
from a PV array must be connected via a dedicated circuit, to a spare fuseway in the main
distribution unit, or to a fuseway in an additional dedicated distribution board.
An inverter supplied from a PV array must preferably be installed in a
dedicated circuit in which:
no current-using equipment is connected, and
no provision is made for the connection of current-using equipment,
and
no socket-outlets are permitted.
An inverter must not be connected by means of a plug with contacts
which may be live when exposed.
Where an electrical installation includes a PV power supply system
without at least simple separation between the a.c. side and the d.c.
side, an RCD installed to provide fault protection by automatic
disconnection of supply must be type B RCD according to BS EN 60898
(IEC 60755, amendment 2).
a.c. cables are to be specified and installed in accordance with BS 7671
So in order to comply with this and BS7671s requirements it would be very hard to comply on a pre existing cable
Should be noted that the draft update to the DTI guide if it passes in its current form no longer uses the word preferably and has been changed to should.
Looked further into MIS3002 and found on page 8:
Furthermore an inverter supplied
from a PV array must be connected via a dedicated circuit, to a spare fuseway in the main
distribution unit, or to a fuseway in an additional dedicated distribution board.