Hi the inverter shutts down for a few mins then trys to reconnect ,only happends on a sunny day, the error code on sunny explorer is Grid Fault 1, the mains supply stays on. It does say on the inverter that the incoming voltage to high(I think} I am at the moment getting the DNO to suply me with a moniter for 14 days to chece the incoming voltageGrid fault 1 on a 4000tl is
The grid voltage has exceeded the permissible range. this error can have the following causes :
The grid voltage at the point of connection of the inverter is too high
or
Grid impedance at the connection point of the inverter is too high
Now you say that the DNO are going to supply you with a meter to monitor the grid voltage? have you been having problems before with overvoltage before for them to to supply this.
Are you close to your local DNO transformer? sometimes this can explain overvoltage if your property is right next to the transformer
As i said before it is possible for the DNO to turn down the voltage going to your property, if you can prove that your supply is outside their regulations.
This is all very simple stuff for your installer or local electrician to check and help you resolve this issue.
Ask your installer to check the fault list from the inverter. This will give a good pattern of when and exactly at what times these faults are happening. This can be done with a laptop with bluetooth, or any of the sma communication range ie sunnybeam.
I can understand where you are coming from,but will not the inverter assume the correct cable will have been fitted in the first place, so, say grid voltage too high
The inverter does not Know what size of cable is fitted it only looks for the correct ranges for its transmission back to the Grid
The max input size for cable on the 4000tl is 10mm
---------- Post Auto-Merged at 15:16 ---------- Previous post was made at 15:08 ----------
Hi are you saying if I find another reason for the inverter triping ,say inverter is set at the wrong settings for a high DNO voltage supply,then I have no need to replace the cable.