Hello Mcgaw, as the others have said 2.5mm is a tad small IMHO?but as it is already fitted best you can do is stick on a 20A MCB:|
but we can back track though a few calcs to check what max power you can draw and still be within permitted Volt drop limits.
Assuming the following facts..
SWA Cable run:
18m SWA is full run from CU to out building.
13m x 2m outbuilding has SWA enter at one end of the 13m building.
If taking 20amp up 18m of 2.5m volt drop = 6.5v
Lighting:
3 x 5ft florries, (single or doubles?) assume doubles 6x 58watt tubes 348watt, 1.5amps.
Any external security light, maybe allow 150watt small flood, 0.65amps.
Total lighting load less than 2.25amp.
13m building one light in middle 2 lights 3m in from each end, total cable run approx 12m cables, including drop down wall to connect to incoming SWA.
If wired in 1.5mm lighting in the building would drop 0.8volt.
Power
Assuming the 6xD/S are radial around side of room, say up one 13m wall around top and part way back down other wall.. around 20m.
Is there any Heating going to be plugged in?
If we need 2.25amp for our lights that leaves 17.75amps on our sockets. (4.0Kw)
If sockets wired in 2.5m, @ 17.75amp over 20m volt drop = 6.4volt
So adding our bits together.
lighting volt drop will be 6.5+0.8=7.3v 3.2%
[max permissible 6.9v]
Power volt drop will be 6.5+6.4=12.9v 5.6%
[max permissible 11.5v]
If running to full power on 20amp MCB then the volt drop would be a tad high?
Now saying that if the florries are just single tubes & no security light and only drawing 3.0Kw on sockets then you are going to be just under & ok!
If you put SWA into a 2way CU in the outbuilding & stick a 16amp on for the sockets. should do the trick but...
advise the customer if it keeps tripping he will need a bigger cable put in.
you could always run another SWA and split lights & sockets via their own SWA at a latter date if it becomes a problem of nuisance overload tripping.