You are forgetting to apply diversity.Thanks ProDave - this is how we were working out the overall breakdown (which is probably excessive but more worse case scenario):-
Exterior Lighting - max 2kW total:-
- 2 x 200w flood lights
- 2 x 100w up/down lights
- 16 x 50w uplighters (run on 12v transformers)
In Outbuilding - max 10kW total:-
- Heater 2000w
- Kettle 3000w
- PC 150w
- Power tools x 2 3200w (1600w each)
- Lights inside shed - 150w
- other small electrical items - 200w
Think you're right about running a dedicated network cable down as we'll have a trench anyway!
Special Location: the lights furthest from the shed are only the 12v 50w, the flood lights will be on/near the shed.
Diversity basically allows you to down rate a circuit on the basis that not everything is on at the same time.
For instance it would be very unlikely to have the kettle on at the same time as everything else. you STOP working for a tea break!!
So I would think a 3KW radial socket circuit would suffice, and look long and hard at your lighting requirements. I know they are "old fashioned" but one or two 58W 5ft flourescents would give you plenty of light in a shed, and low energy outside lighting as well.