Just wondering what you would put on PIR. Supply to separate DB is two 10mm twin and earths ran together, never seen it before ?:|
Hi Dobo99
The regs you need to check.. to make sure your installation complies with 17th BS7671 are as follows...
Page 75:-
433.4 Overload protection of conductors in parrallel.
433.4.1 Equal current sharing between parallel conductors.
433.4.2 Unequal current sharing between parallel conductors
Page 76:-
434.4 fault current protection of conductors in parrallel.
Page 104:-
523.8 current carrying capacity of cables conductors in parallel.
As a quick guide....
# It is preferable to have same CSA, material, & length of parallel conductors
# NO branches in one leg of parallel conductor. {excluding ring circuits!}
# You should balance load equally across conductors.
# You can have single protection device.
# If single protective device not effective then multiple protective devices for each leg of parallel conductor.
# For more than two conductors in parallel a fault protective device shall be fitted at supply and load both ends of each parallel conductor.
# Where adequate current sharing not possible or more than four conductors needed consideration of using bus-bar trunking should be made.
Also Pages 353