Insulation resistance:-With all new wiring Ins Res should be off the scale of the meter no matter how long or short the cables are..
e.g. > 200Mohms or >999Mohms are typical max values on commonly used meters.
so larger than > max readable value is still going to be 'OL' off scale..
you cant get a reading bigger than the biggest readable value.
Continuity:-
Did you zero the leads correctly?
Incorrectly zeroed leads can cause funnies on really short lengths.
e.g.
R1+R2 on 1.0mm T&E is 0.0362ohms per meter
Say two lengths one 5m and one 75m
5m actual R1+R2 would be 0.18ohms
75m actual R1+R2 would be 2.72ohms
lets say meter leads are 0.5ohms when zeroed correctly meter actually reads
{cable+lead-stored zero value}
0.68 - 0.5 = 0.18ohms and
3.22 - 0.5 = 2.72ohms.
BUT
If when zeroing leads you had a bad connection and the meter calculated for 0.75ohms of lead resistance....
when go back to you proper cable tests with a good connection meter would get
{cable+proper lead-incorrect zero value}
0.68 - 0.75 = -0.07ohms
3.22 - 0.75 = 2.47ohms
so on a longer cable length you just get an incorrect R1+R2
but on a shorter cable length you get "Minus 0.07ohms"
Minus figures can mess up some meters and they can end up giving incorrect higher values!
Guinness