Has anybody had any experience with the RCD devices on caravan systems tripping when there is a thunderstorm. It's happenend a couple of times but not being present when this happens makes it hard to solve
Has anybody had any experience with the RCD devices on caravan systems tripping when there is a thunderstorm. It's happenend a couple of times but not being present when this happens makes it hard to solve
No SPD's in the systemJust been reading about SPDs downstream of RCD (eg on telephone supply) causing RCDs to trip
No leaks & it's not necessarily when it's rainingIf it is the same caravan it could just be the van taking in water if there is a deluge. Caravans are known for the odd leak , and condensation.
I'm considering installing an SPD in the caravans consumer unit to deal with any induced voltagesHas anybody had any experience with the RCD devices on caravan systems tripping when there is a thunderstorm. It's happenend a couple of times but not being present when this happens makes it hard to solve
Would using an AC type RCD help here? since it doesn't "see" DC currents.Nuisance tripping (as shown above) is not just limited to serious faults where there are large changes in voltage. If there is sufficient unbalanced noise on the Live and Neutral i.e. the Live and Neutral do not have noise superimposed in an equal but opposing phase, then this will be 'seen' by the RCD as an imbalance especially if high amounts of leakage is 'biasing' the RCD.
What sure does not give the RCD a fighting chance is when such imbalance in the Neutral is created with the use of TNC-S style systems and especially where the Neutral is bonded to Earth at the entrance to the premises. Any noise on the Neutral is transferred to the Earth thus giving the Earth a similar potential to Neutral (the local Earth usually has a higher impedance than Neutral and easily takes on this potential).
The differential mode noise (simply the turning on of a significant load in an adjacent property), which would usually cause equal but opposing disturbances in the Live and Neutral and therefore cancel, is now found as equal and opposing disturbance across the Live and Earth.
This, therefore, presents a case where the Live and Neutral currents flowing through the RCD to Earth (via the filter capacitors) are not equal and opposing, and will be again be interpreted by the RCD as an earth leakage event. In this case the simplest cure is to employ an RCD that ensures the leakage is sustained before activating a trip (please note we do not state removing the RCD!).
This situation can be exacerbated with T-T, Z-T and I-T systems (see here) as the weaker earth systems can easily introduce noise and voltages into the RCD core in the form of unbalanced or common mode currents, especially in the presence of ground gradients (voltages that exist as a result of current flowing through the ground).
Such systems are extremely prone to RCD trips during lightning storms as a result of ground gradients even with cloud-to-could strikes (there is this weird thinking that only cloud-to-ground strikes cause ground voltages!).
But, it does not need a lightning storm; It could well be a neighbour with a problem causing an RCD to trip. If the neighbour has some Live-Earth fault causes voltage gradients in the surrounding earth mass, this is picked up by the T-T system's earth rod and transferred into the RCD as common-mode currents.
A word about 'Electronic' RCDs; These devices, as opposed to the electro-magnetic-mechanical types, are extremely prone to nuisance tripping because they are designed to not only trip during imbalance but also trip if a fault is detected with the incoming supply. Unfortunately, being electronic, these devices have very fast reaction times and will trip even on extremely sharp events such as switching transients. Many a case of nuisance tripping has been resolved by replacing the RCD with the more basic type.
Tony why did need a "motor operated valve" on an overhead supply?
you need2 GDT's on a phone line,in a strike usually both lines rise to the same potential,connect a GDT from A leg to earth and another from B leg to earth and that can prevent it.commonly they are connected across the A and B legs to prevent some idiot shoving 240 up the line,yes it does happen.MOV Metal Oxide Varistor
GDT Gas Discharge Tube
So glad to read this. Have exactly this problem when there's localised lighting strikes and I'm TT.Have been reading a bit more about common mode currents due to lightning strikes causing RCDs to trip in TT systems. It can happen apparently, this from Marc's tech pages http://www.marcspages.co.uk/pq/3342.htm
Would using an AC type RCD help here? since it doesn't "see" DC currents.