Hi,
Ive got to change 2 light fittings for a friend tomorrow and want to do it properly and issue MWC. As when you join a scam they want to see all the previous certs issued?
Ive looked at the current fittings and its a right bodge. Chocolate blocks taped up pushed up into cladded ceiling. Im gonna replace these with wagos.
What tests do I need to carry out is it
R1+R2 at the fittings
IR - can I do L&NtoE to avoid having to take bulbs out etc
Zs
Theres no rcd present but as im not altering the circuit I dont need to fit one do I. Im changing like for like and its not in a special location. On the certs I have (NIC Green ones) it asks for RCD details etc. Do I put N/A
Thanks for any advice