I know everyone has different opinions as to codings and arguments often ensue.
However
I have carried out an EICR which has uncovered a list of C3's as long as your arm
But there are a few that I am unsure of how to grade.
The oven and immersion are both wired from the same ring
(the immersion is wired in brown and blue)
A standard wall light is mounted just on the edge of zone 2 in the bathroom
There is a low insulation resistance reading (0.42M ohm) on one socket circuit (I have unplugged all surge plugs and there are no rcd sockets that I can find)
Unearthered metal fittings (cabling is earthed but not connected to fittings)
Bonding is ok and one 30ma RCD covers whole board
Any views?