Hi all, this is my first ever post so be do not all jump on me!!
Anyway, i have to run a 25mm TP+N [100meter long] submain from a free standing meter compartment across a plot of ground to some wooden sheds. No extraneous conductive parts at all in any of them at all, apart from possibly in the very last, 100 metre away shed [supply is PME by the way] Anyhow, i do not want to get into all the usual arguments about exporting earths Vs TT !!! The incoming supply neutral is 35mm, so my earth bond [from 54.8] needs to be 10mm. As, happily, my cable is 25mm, can i use a 5 core cable and use the 5th core as a combined CPC and equipotential bond [in parallel with the cable armour i suppose] or does the bonding cable have to be a separate conductor from the CPC I can find nothing at all in the BRB concerning this at all.
Thanks all...
Anyway, i have to run a 25mm TP+N [100meter long] submain from a free standing meter compartment across a plot of ground to some wooden sheds. No extraneous conductive parts at all in any of them at all, apart from possibly in the very last, 100 metre away shed [supply is PME by the way] Anyhow, i do not want to get into all the usual arguments about exporting earths Vs TT !!! The incoming supply neutral is 35mm, so my earth bond [from 54.8] needs to be 10mm. As, happily, my cable is 25mm, can i use a 5 core cable and use the 5th core as a combined CPC and equipotential bond [in parallel with the cable armour i suppose] or does the bonding cable have to be a separate conductor from the CPC I can find nothing at all in the BRB concerning this at all.