I'm presently working on a restaurant renovation and there are two sets of contractors working on site. One responsible for the front of house. The others fitting the commercial kichen and extraction. I'm not particularly happy with the standard electrical work on the kitchen side of things. Specifically on how the ventilation system has been installed. So I thought I'd ask the following questions to see if I'm being a nag unnecessarily.
Here's the set up as is...
Four fans in the roof. All single phase. One air intake. Three extract
The largest fan is the kichen range extractor. Rated at 11.5 amps
The other fans are all smaller in size and rated 4.5 amps.
The kitchen extractor is wired from the distribution board via a 20a mcb directly to the gas interlock. And then onto the fan via a speed control unit.
The other three fans are wired via one 20 A mcb to three switched fcu's using 2.5 t+e. Then onwards to the fans. One goes via another gas interlock system.
Hope that info makes sense.
So my concerns are around safe isolation and maintenance. In my world I would have provided each fan with its own mcb. And connected each fan to an isolation switch (marked with a 1 and 0) and then on to the control switches and gas interlocks etc...
Section 537.3 seems to be the relevant section. Specifically as there are rotating parts and the isolation points as installed are remote from the fan units.
So the question. Anyone happy with as installed? Are there any other regs that are pertinent ? Or should I just mind my own business as its not my job.
Here's the set up as is...
Four fans in the roof. All single phase. One air intake. Three extract
The largest fan is the kichen range extractor. Rated at 11.5 amps
The other fans are all smaller in size and rated 4.5 amps.
The kitchen extractor is wired from the distribution board via a 20a mcb directly to the gas interlock. And then onto the fan via a speed control unit.
The other three fans are wired via one 20 A mcb to three switched fcu's using 2.5 t+e. Then onwards to the fans. One goes via another gas interlock system.
Hope that info makes sense.
So my concerns are around safe isolation and maintenance. In my world I would have provided each fan with its own mcb. And connected each fan to an isolation switch (marked with a 1 and 0) and then on to the control switches and gas interlocks etc...
Section 537.3 seems to be the relevant section. Specifically as there are rotating parts and the isolation points as installed are remote from the fan units.
So the question. Anyone happy with as installed? Are there any other regs that are pertinent ? Or should I just mind my own business as its not my job.