so how would PME/TNCS be any different?But one disadvantage of TT is that if for some reason an RCD fails you will have no earth protection. With an earth resistance of 100 ohms an earth fault current would be just over 2 Amps, this would not trip any MCB and any metal would be at 230 volts until someone touched it.
RCD's are meant as a backup to MCB's or fuses and not as a primary and only source of earth fault protection.
That's the way I was taught anyway.
no. it wont be at 230v. it will be much lower (after all, touch voltage should be limited to 50v by design)With an earth resistance of 100 ohms an earth fault current would be just over 2 Amps, this would not trip any MCB and any metal would be at 230 volts until someone touched it.
and the difference with an RCD failing on PME is.?So if I have a circuit say a lighting circuit with metal switches, The RCD fails and so I am relying on MCB protection.I get an earth fault on the light and the switch becomes live, The live current will flow back to the board and down the earth rod at roughly 2 Amps.
This will not trip a 6A MCB. So the light switch will be at 230V until someone touches it.
Where am I wrong with this argument?
wish I was a plumber and able to put into words,Well you need to remember that we need to create an equipotential zone, so there should be little risk of hand to foot shock. the risk would be between hand to hand where we may be in contact with an exposed conductive part and simultaneous in contact with an extraneous conductive part which is not bonded at therefore at different potentials.
Excellent cheers. Equipotential zones, I guess with a TT they are extra important.Well you need to remember that we need to create an equipotential zone, so there should be little risk of hand to foot shock. the risk would be between hand to hand where we may be in contact with an exposed conductive part and simultaneous in contact with an extraneous conductive part which is not bonded at therefore at different potentials.
If an RCD fails on PME and there is an earth fault the earth fault resistance is so small it will allow a very high fault current to flow tripping the MCB's in the correct time and cutting the circuit dead.and the difference with an RCD failing on PME is.?
your arguement only stands good until you lose a neutral, which is a bigger probability than having a failed RCD,If an RCD fails on PME and there is an earth fault the earth fault resistance is so small it will allow a very high fault current to flow tripping the MCB's in the correct time and cutting the circuit dead.With a TT the earth fault path resistance is so high it would never trip any MCB. MCB's would only trip on a a phase to neutral fault not a phase to earth fault.
This is true
But a well designed tt system is safe.
Steps I am trying to understand this on a modern house with plastic services. If you loose the incoming neutral surely nothing will work because the circuit is no longer a circuit. The neutral and cpc's are seperate on consumer side so how can the earth rise to 240 volts as it seperate to the neutral?your arguement only stands good until you lose a neutral, which is a bigger probability than having a failed RCD,then no matter what happens on a PME everything that is earthed will go to 230v potential and will not be able to blow either RCD or MCB until someone touches it.
My heart rate doubled when I read that, then I looked at the page count. I almost stopped reading that mid sentence and ran away.I think PME is better than an earth spike, does anyone disagree with anything I have said?
If the neutral is lost on the network then you also lose the earth so the metalwork potential rises to 230V because of the N-E link in the head.If you loose the incoming neutral surely nothing will work because the circuit is no longer a circuit. The neutral and cpc's are seperate on consumer side so how can the earth rise to 240 volts as it seperate to the neutral?
a poorly designed installation that no matter the earthing arrangements would make no different.My heart rate doubled when I read that, then I looked at the page count. I almost stopped reading that mid sentence and ran away.If the neutral is lost on the network then you also lose the earth so the metalwork potential rises to 230V because of the N-E link in the head.
If you simply lost the neutral between the head and CU then what you say is correct.
Dont you dare drink all the ruddy GuinnessGuinnessGuinnessGuinnessYes, Steptoe.I feel another long thread coming on.........more Guinness required.
My thread http://www.talk.electricianforum.co.uk/showthread.php?t=1559A link would be great, this is new to me cheers.
well that will be a few hours of la timeMy thread http://www.talk.electricianforum.co.uk/showthread.php?t=1559The big one that came before http://www.talk.electricianforum.co.uk/showthread.php?t=483
Did I tell you I have memorised BOTH of those threads off by heart..well that will be a few hours of la time
deke and brian allways scof all the meds befor anyone gets emDid I tell you I have memorised BOTH of those threads off by heart..I can quote em verbatim word for word!!!
Go on ask me..
what the 475th word?????????????????
O) :Blushing
Has admin been round yet with the medication trolley yet?
if yes.....
think he missed me again?
:_| :_| :_|