Had to go and find out why a local garage had lost all power .
Tested between 3 phases at service meter and nothing on L1 , 415v on L2 and L3 ,230v between L2 / N and L3/N . so came to conclusion that phase lost on supply side.
What im confused by is that obviously some of the installation will be single phase ( office , reception , etc ) so why was power lost on 1 phase affected the whole installation , thought the single phase circuits would still be ok.
Not really had much 3 phase experience.
any help would be great as i told owner of building to contact supplier as phase lost , but now i think i may have missed something .