So I've just completed (well apart from this issue) an installation for a coffee shop/cafe. It's all tubed out in galv conduit, as the client wanted the 'industrial' look.
The circuit thats being problematic is the lighting. I have created pendants from thru boxes on the ceiling, which drop to metal E27 holders, via 0.75 3 -core flex. All holders have correct polarity and really good r2. All meggerred A:OK between all lines and conduit etc
So take the bank of 8 pendants in the window for example. Disconnect switched live from light switch over at the grid, with no lamps in, L-E is open circuit. Put your first lamp in and its 150ohms, stick another lamp in and it reduces to about 75 - you keep adding lamps until eventually the circuit has a low enough resistance to throw the breaker.
I nit picked through it for hours today, with a rather worried client looking on as he needs to open (the woes of commercial work!)
Could it be related to the fact that at the origin of the supply, there is a reading of about 0.25 between neutral and earth. Putting a lamp in makes a pathway between L and N so therefore to earth as well?
I need to look at it with a fresh head on Monday really, but thought i'd see what others think.
Cheers
The circuit thats being problematic is the lighting. I have created pendants from thru boxes on the ceiling, which drop to metal E27 holders, via 0.75 3 -core flex. All holders have correct polarity and really good r2. All meggerred A:OK between all lines and conduit etc
So take the bank of 8 pendants in the window for example. Disconnect switched live from light switch over at the grid, with no lamps in, L-E is open circuit. Put your first lamp in and its 150ohms, stick another lamp in and it reduces to about 75 - you keep adding lamps until eventually the circuit has a low enough resistance to throw the breaker.
I nit picked through it for hours today, with a rather worried client looking on as he needs to open (the woes of commercial work!)
Could it be related to the fact that at the origin of the supply, there is a reading of about 0.25 between neutral and earth. Putting a lamp in makes a pathway between L and N so therefore to earth as well?
I need to look at it with a fresh head on Monday really, but thought i'd see what others think.