i popped in on friday and found
1 phase at 5.4 amps
2 phase at 5.2 amps
3 phase at 10.8 amps (the problem phase)
so i moved the cables to a spare way it was a 4 phase contactor and it dropped down to 7.8 amps
i asked the mechanics to keep an eye on it (yeah i know fat chance) and we will pop in on tuesday to check.
it was going 1-2 times a day they said but not everyday
all connections at board and contactor were tight when checked