Hi all..A question re testing a standard radial BUILT IN oven circuit for an EICR in terms of what's expected/best practice...
Assuming I can access the oven connector unit in a cupboard next to the oven as the final connection point.. its my understanding that to do both dead R1+R2 and a MEASURED live Zs, I can take both these readings at the connector unit and record these both..yes? (House is on a TT so I do insist on taking measured Zs throughout whatever the 'advice' may be from up top re working live!)
BUT...given that the R1+R2 test is actually all about proving CONTINUITY of the cpc, surely the tests I've mentioned don't actually prove this??!..
So..would it be advisable as well as the recorded tests above to just do a continuity test say between the metalwork of the oven at the cpc at the connector unit just to prove to myself as the tester that the earth IS then continuous?
Hope that all makes sense!..any thoughts gratefully received.
Assuming I can access the oven connector unit in a cupboard next to the oven as the final connection point.. its my understanding that to do both dead R1+R2 and a MEASURED live Zs, I can take both these readings at the connector unit and record these both..yes? (House is on a TT so I do insist on taking measured Zs throughout whatever the 'advice' may be from up top re working live!)
BUT...given that the R1+R2 test is actually all about proving CONTINUITY of the cpc, surely the tests I've mentioned don't actually prove this??!..
So..would it be advisable as well as the recorded tests above to just do a continuity test say between the metalwork of the oven at the cpc at the connector unit just to prove to myself as the tester that the earth IS then continuous?
Hope that all makes sense!..any thoughts gratefully received.