cooker calculation - 3 phase

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

matt.leung

Well-known member
Joined
Feb 26, 2009
Messages
1,062
Reaction score
0
Location
Bromley, Kent
Hi all,

Just trying to get my head around this calculation and would be greatful for any guidance.

i have a 3phase 60,000w cooker and just trying to work out the current.

60,000 / 230v = 260.86A per phase

60,000 / 415v = 144.58A per phase

what am i doing wrong, because the numbers seem very high. have i missed out a step?

 
60,000/230 =260.86A per phase, single phase.

60,000/400/1.73 = 86.7A per phase 3 phase (1.73 is the square root of 3)

BUT 60KW is a BIG cooker. Are you sure that figure is correct? Must be some commercial monster.

 
I agree with Dave ..... I think you have mis-read the rating ....... 180kW of cookers in a pub kitchen? Thats gonna be one hell of a hot place to work!

Also, not many pubs can support almost 270A per phase just for the cookers!

 
I did a job once that had four x 100 amp three phase cookers incoming supply was 200 amp and as you may guess they had regular call outs from DNO. I did tell them before they had the work done it wouldn't work but some people think they know better.

 
Matt, are you sure they're not industrial furnaces !!!! That cannot be right .

Check the ratings mate, then try the following.

Line Amps =

KVA X 1000

----------------------

Line Volts X 1.73 X pf

 