Just in the process of changing a board 2 cooker circuits 1 lighting and 1 socket circuit. 1 of the cooker circuits trips the rcd when the mcb is switched on, tested IR to earth and it's over 100meg, tested for borrowed neutrals and there are non? With the isolator off the rcd stays on but as soon as you switch it on it trips? Cooker IR's out fine, even with termostats on, rcd trips at correct times and at 23mA on ramp test, tested the 2g isolator and it tests out fine? Any ideas?