H4 Cooker circuits in household and similar premises
The circuit supplies a control switch or a cooker unit complying with BS 4177, which may incorporate a socket-outlet.
The rating of the circuit is determined by the assessment of the current demand of the cooking appliance(s), and cooker control unit socket-outlet if any, in accordance with Table A1 of Appendix A. A 30 or 32 A circuit is usually appropriate for household or similar cookers of rating up to 15 kW.
A circuit of rating exceeding 15 A but not exceeding 50 A may supply two or more cooking appliances where these are installed in one room. The control switch or cooker control unit should be placed within 2 m of the appliance, but not directly above it. Where two stationary cooking appliances are installed in one room, one switch may be used to control both appliances provided that neither appliance is more than 2 m from the switch. Attention is drawn to the need to provide selective (discriminative) operation of protective devices as stated in Regulation 536.2.
On-Site Guide 18