phil d
Well-known member
Went to give my mate a lift with a job over the weekend, doing some much needed repairs on a rather scruffy commercial job. Part of it was replacing some light fittings, the whole place was lit with pendants containing CFL's, now he reckoned he got a belt after he touched 2 earths on a fitting, the circuit was live, he split the earths and got a belt. Ok so here we go, we disconnect the earth at the CU and measuring between this cable and either the earth bar or the neutral bar we were getting around 140 volts on a Fluke multimeter, the more lights you turned on the higher the voltage, peaking at around 170 volts, measure the current and it was around 30 milliamps, old 3036 board no RCD's, we plan to change this board shortly. we IR the circuit and are getting around 35 meg at 500v, start breaking it down and testing the cable between fittings and it's megging clear. we find a couple of rough joints and replace them, also we remove a couple of redundant fittings, power it back up and we have the same readings as before. Anyway to prove a point I end up getting an RCBO and wiring it in using a couple of bits of cable, ramp testing it with nothing on the outgoing terminals and it trips at 22 milliamps, I connect this into the circuit and go to the furthest fitting where I conduct a ramp test and get 22 milliamps tripping current, clearly despite the meter readings I am not actually getting what I appear to be seeing. I have had induced voltages on cables before but never anything like this, if I had the perceived 30 milliamp leakage down the earth then it would/should have taken out the RCBO, but it didn't, wonder if the Fluke is faulty?